• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Industrial Ventilation Rate

Mech

REGISTERED
Joined
Oct 30, 2009
Messages
1,054
Location
Eastern PA
'09 IBC & IMC

21,000 sf building

F-1

What outside air ventilation rate would you use for plastics extruding?

Thanks
 
$ $ $

From the `09 IMC, Section 403.3:__"Ventilation rates for occupancies not

represented in Table 403.3 shall be those for a listed occupancy classification

that is most similar in terms of occupant density, activities and building

construction; or shall be determined by an approved engineering analysis."

Also, ...

From the `09 IECC, Section 503.2.1:__Calculation of heating and cooling loads:

"Design loads shall be determined in accordance with the procedures described in

the ASHRAE / ACCA Standard 183.......Heating and cooling loads shall be adjusted

to account for load reductions that are achieved when energy recovery systems

are utilized in the HVAC system in accordance with the ASHRAE HVAC Systems

and Equipment Handbook.......Alternatively, design loads shall be determined by

an approved equivalent computation procedure, using the design parameters

specified in :Next('./icod_iecc_2009_3_par001.htm')'>Chapter 3."

IMO, ...an engineered analysis & design will be required.



& & &
 
Back
Top