We are adopting the 2009 energy codes which will require insulated headers. Does anyone have some good examples of these? Im thinking 2- 2Xs with foam board sandwiched between or a another code compliant method for this. Thanks in advance.
they are not required to be what Mark posted.steveray said:Where is the header insulation required in the 2009 IECC?
Not correctsteveray said:...No "open" corners R602.10.4.4(1)
I believe the 2012 changes the corner requirements and a strap will be required.guys around here don't want to mess with any more straps
Yay!...More reason for them to hate me! Having a hard enough time beating the 09 into their heads since last February.mtlogcabin said:I believe the 2012 changes the corner requirements and a strap will be required.
depends on where. state of washington requires R10 insulated header....mtlogcabin said:they are not required to be what Mark posted.Table 402.4 requires headers to be insulated. It does not tell you what kind of insulation.
Yes See the following code sectionMcShan said:Can the single header by site built in your opinion?
Open corners are allowed. See Figure R602.10.4.4(1), detail (a)outside corner. It states "orientation of stud may vary. See figure R602.3(2)." Figure R602.3(2) shows different configurations of corner and partition posts.steveray said:Typically we end up with panel to panel, guys around here don't want to mess with any more straps...I guess I should have said that open corners are more the exception than the norm now....I don't feel old enough to have seen 3 stud corners go to 2 stud corners and now back to 3...