This project is in Jacksonville Florida, so governing code is the 2020 Florida Building Code, Energy Conservation, 7th Edition.
I have a tenant that is located in the middle of a single story industrial flex building. The tenant separation walls are 1hr rated (to underside of deck) with an R-19 insulation. The tenant space is divided into warehouse and office. Does the wall separating the office and warehouse need to go to deck? We have a third party reviewing the drawings for permit, and they are saying it is required, but the contractor we are using is saying that they have never had to provide a full height insulated wall to meet the energy code before. The permit review company is citing C402.2.1 Roof assembly: The minimum thermal resistance of the insulating material installed either between the roof framing or continuously on the roof assembly shall be specified in Table C402.1.3, based on construction materials used in the roof assembly. Insulation installed on a suspended ceiling having removable ceiling tiles shall not be considered as part of the minimum thermal resistance of the roof insulation. Continuous insulation board shall be installed in not less than 2 layers and the edge joints between each layer of insulation shall be staggered.
The shell building meets the requirement of table C402.1.3 with insulation entirely above deck at an R-25ci, but the walls are tilt and the owner forewent the insulated panels. I will run the energy calcs with Comcheck, and maybe that will the proof in the pudding, but does anyone know of any specific code requirement that requires insulated walls between conditioned and unconditioned space?
I have a tenant that is located in the middle of a single story industrial flex building. The tenant separation walls are 1hr rated (to underside of deck) with an R-19 insulation. The tenant space is divided into warehouse and office. Does the wall separating the office and warehouse need to go to deck? We have a third party reviewing the drawings for permit, and they are saying it is required, but the contractor we are using is saying that they have never had to provide a full height insulated wall to meet the energy code before. The permit review company is citing C402.2.1 Roof assembly: The minimum thermal resistance of the insulating material installed either between the roof framing or continuously on the roof assembly shall be specified in Table C402.1.3, based on construction materials used in the roof assembly. Insulation installed on a suspended ceiling having removable ceiling tiles shall not be considered as part of the minimum thermal resistance of the roof insulation. Continuous insulation board shall be installed in not less than 2 layers and the edge joints between each layer of insulation shall be staggered.
The shell building meets the requirement of table C402.1.3 with insulation entirely above deck at an R-25ci, but the walls are tilt and the owner forewent the insulated panels. I will run the energy calcs with Comcheck, and maybe that will the proof in the pudding, but does anyone know of any specific code requirement that requires insulated walls between conditioned and unconditioned space?