• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Insulating spec warehouse buildings

Nicole Brooks

Registered User
Joined
Sep 21, 2018
Messages
67
Location
Baltimore
I work for a developer that builds industrial flex buildings. My question is if the shell building meets all the requirements of the IECC, when a new tenant leases a first generation space that does not require a conditioned warehouse, but the office portion of their space is conditioned, is there a requirement for a full height insulated wall between the office portion and the warehouse? Orr, because the shell meets the requirements of the code, no additional insulation is required?
 
, because the shell meets the requirements of the code, no additional insulation is required?
It would be nice if that were the case but the details called out in the shell building really matter because the IECC sucks:

C505.1 General


Spaces undergoing a change in occupancy that would result in an increase in demand for either fossil fuel or electrical energy shall comply with this code (meaning "as new").

[A] CHANGE OF OCCUPANCY. Any of the following shall be considered as a change of occupancy where the current International Building Code requires a greater degree of safety, accessibility, structural strength, fire protection, means of egress, ventilation or sanitation than is existing in the current building or structure:
  1. Any change in the occupancy classification of a building or structure.
  2. Any change in the purpose of, or a change in the level of activity within, a building or structure.
 