In an effort to meet IMC 602.2.1 Materials exposed within plenums, is acceptable to wrap hydronic pvc pipe with ASTM 84 E 25/50 Flame/Smoke rated insulation per:
602.2.1 Materials exposed within plenums.
Except as required by Sections 602.2.1.1 through 602.2.1.5, materials exposed within
plenums shall be noncombustible or shall have a flame spread index of not more than
25 and a smoke-developed index of not more than 50 when tested in accordance with
ASTM E 84.
602.2.1 Materials exposed within plenums.
Except as required by Sections 602.2.1.1 through 602.2.1.5, materials exposed within
plenums shall be noncombustible or shall have a flame spread index of not more than
25 and a smoke-developed index of not more than 50 when tested in accordance with
ASTM E 84.