• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

interesting calif thread

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
a technology question and interp question::

http://www.eng-tips.com/viewthread.cfm?qid=276688&page=1

any calif's out there???

""""""""California requires a complete coverage system, and NFPA 72, 5.5.2.1 states: "If required and unless otherwise modified by 5.5.2.1.1 through 5.5.2.1.5, total coverage shall include all rooms, halls, storage areas, basements,attics, lofts, spaces above suspended ceilings, and other subdivisions and accessible spaces...."We and all our AHJ's have as long as I can remember protected these spaces with heat detection. Are you saying that that is not required? I'd like to know how that works.""""""""""
 
In that other thread, someone posted:

1006.2.4.2.2.1.1 [For SFM] Automatic Detection. Smoke detectors shall be used as the primary method of automatic alarm initiation except in areas where the environment or ambient conditions exceed smoke detector installation guidelines; another method of automatic detection shall be used. In areas containing sprinklers, heat detectors may be omitted. Smoke detectors shall be designed, installed and maintained in accordance with NFPA 72 as amended in Article 91.
This talks about SMOKE detectors, not heat detectors, unless smokes are not suitable. An above ceiling space is not necessarily outside the limits of a smoke detector. The heat detectors discussed probably do not meet this requirement. Confirm if the section calling for "total coverage" is specifically requireing SMOKE detection, or more generic FIRE detection.

Whether it is smokes or heat, the detection is required above suspended ceilings.
 