Interior Ramp Clearance

CAR

SAWHORSE
Joined
Feb 14, 2019
Messages
48
Location
Chicago, IL
9tXwqkPXXrmHp3nN6


Hello,
I am working on an interior office renovation where the client wants to add a fitness room and lockers to their existing office. The fitness area will have a raised specialty floor 5" high. So we're ramping down from the fitness area to a corridor that takes you into the men's and women's lockers in each side. To get into each locker room we have vestibule. This vestibule consists of an opening with no door at the bottom of the ramp. My question is. How much clearance do I need from bottom of ramp to the vestibule opening on each side? As of now we have 2'-0" clear from B.O. ramp to the start of the opening. I would've preferred 4'-0" but the space is tight and the client's demands for constant changes have left us with not a lot of wiggle room. Now this client is asking why we're even having the 2'-0" clearance before the openings. I've looked online but I only find examples of ramps with adjacent doors (which show a minimum of 2'-0"). I have not found any references to cased openings without doors. Does anyone know what is the minimum distance allowed from the B.O. ramp to these openings? Not sure if anyone can see the image I tried to paste.

Thank you.

7m88RPb2EdSTnsfA9
 
Last edited:
Unless you are a paid member, you cant post images except by external webpage link.

The small cost of joining is easily recuperated by the wealth of knowledge here. Sawhorse link in my signature will get you to the spot.
 
48 inches is required. Per ANSI A117.1, Figure 404.2.3.4(a), a 48-inch maneuvering clearance is required at openings without doors for the full width of the opening. Per Section 404.2.3.1, a maneuvering clearance cannot have a slope steeper than 1:48.
 
Unless you are a paid member, you cant post images except by external webpage link.

The small cost of joining is easily recuperated by the wealth of knowledge here. Sawhorse link in my signature will get you to the spot.

I see. Thank you.
 
48 inches is required. Per ANSI A117.1, Figure 404.2.3.4(a), a 48-inch maneuvering clearance is required at openings without doors for the full width of the opening. Per Section 404.2.3.1, a maneuvering clearance cannot have a slope steeper than 1:48.

Thank you for the prompt reply.
 
If the opening is 60" you are good......

Thanks. One thing I'm wondering is that we have 2' from where the ramp ends to where the opening begins. I've been trying to post photos ever since I upgraded my account yesterday but it doesn't seem to be working. Anyway, this client wants to take away the 2' and just have the bottom of ramp to align with the start of the opening. I don't want someone in a wheelchair to make a turn while there's still a slope. I keep trying to find that scenario in the code. But I only see when there is a door present you need 24" min between the door and ramp. So this is the approach I took in this instance.
 
I don't see a problem with what you posted in post#10. If there were doors there instead of opens then it would be a different animal. IMHO
 