IBC (2015 Ed.) requires an intermediate handrail such that all required "egress width" for a stairway be located within 30" of a handrail (1014.9) as does NFPA 101 (2015 Ed.) 7.2.2.4.1.2 (1). In addition, NFPA 101 clarifies that the minimum clear width between intermediate handrails shall be not less than 20" (7.2.2.4.1.3).
Does the IBC have a similar provision that clarifies the minimum width between handrails when an intermediate handrail is used? I couldn't find one.
Note, the building is fully sprinklered so it is my understanding that under exception (2) the 48" minimum width between handrails required for a stair to be "accessible" per 1009.3 does not apply. Correct?
Thanks.