Intermediate handrails required at landing or not?

ADAguy

REGISTERED
Joined
Sep 11, 2013
Messages
6,307
Location
California
upload_2017-7-26_8-2-20.png

MH, way back in 06? I believe you responded to a question similar to this.

So say you as to whether an intermediate handrail is also required at 45 degrees at the corner of the landing?
Or, no intermediate as the landing could be seen as monumental in width with pairs of handrails required on each side of the landing only?

I believe code required handrails on both sides of a stair as the stair has but the landing does not, or should it?

Also, is the handrail extension in fact a projection (>4") at the landing?
 
1. Yes, there should be a intermediate rails.
2. Yes, there should be several intermediate rails at the Bottom.
3. The extensions of the handrails, as shown, are not in the normal POT but the intermediate rails should "loop" below 27 inches due to projection issues.



Based on the code section and definition listed below
1014.9 Intermediate handrails
Stairways shall have intermediate handrails located in such a manner that all portions of the stairway minimum width or required capacity are within 30 inches of a handrail. On monumental stairs, handrails shall be located along the most direct path of egress travel.
STAIRWAY. One or more flights of stairs, either exterior or interior, with the necessary landings and platforms connecting them, to form a continuous and uninterrupted passage from one level to another.
FLIGHT. A continuous run of rectangular treads, winders or combination thereof from one landing to another.
pgA5_figA4.gif

ewc.jpg
 
I don't think you would want the intermediate rail at a 45. I would continue it parallel to the wall, with a break at the landing.
 
The handrail is not required to be continuous along the landing. Using the 2015 IBC as an example:

https://up.codes/viewer/general/int_building_code_2015/chapter/10/means-of-egress#1014

1014.6 Handrail Extensions

Handrails shall return to a wall, guard or the walking surface or shall be continuous to the handrail of an adjacent flight of stairs or ramp run. Where handrails are not continuous between flights, the handrails shall extend horizontally not less than 12 inches (305 mm) beyond the top riser and continue to slope for the depth of one tread beyond the bottom riser. At ramps where handrails are not continuous between runs, the handrails shall extend horizontally above the landing 12 inches (305 mm) minimum beyond the top and bottom of ramp runs. The extensions of handrails shall be in the same direction of the flights of stairs at stairways and the ramp runs at ramps.

The important part to note is that the handrail is not required to be continuous provided that it complies with the handrail extension requirements at the top and bottom of the landing. This is largely to avoid tripping hazards. Please note that intermediate handrails are only required when the full width of the stair is necessary for egress capacity. For example: if you have a 60 inch stairway but only required 30 inches for capacity you could do a single rail on both sides as the required capacity is only for 30 inches of the stairway and those occupants will be within the 30 inch threshold to avoid the intermediate handrail requirement (I would confirm with the A of R as there have been a number of lawsuits related to people tripping around NYC recently where intermediate handrails were not provided).

The concept behind the intermediate rail is that it allows for greater egress travel during emergencies as most people are attracted to handrails for guidance. If an intermediate handrail is not made available, occupants will most likely not use the center of the stairway.
 