In areas prone to wildfires, protecting buildings from the spread of fire is crucial. The 2024 ICC Wildlife Urban Interface Code provides specific guidelines to enhance the fire resistance of structures. One critical section of this code is 504.3, which focuses on the protection of eaves and soffits. This article will explain the requirements of Section 504.3 and the associated commentary to help you understand how to protect these vulnerable parts of a building effectively.
Section 504.3: Protection of Eaves
Understanding the Code:
Section 504.3: Protection of Eaves
Code Requirements:
- Exposed Underside Protection:
- Materials:
- Ignition-resistant materials, or
- Materials approved for not less than 1-hour fire-resistance-rated construction, or
- 2-inch (51 mm) nominal dimension lumber, or
- 1-inch (25 mm) nominal fire-retardant-treated lumber, or
- 3/4-inch (19.1 mm) nominal fire-retardant-treated plywood.
- Identification:
- The fire-retardant-treated plywood must be identified for exterior use and meet the requirements of Section 2303.2 of the International Building Code.
- Materials:
- Fascias Protection:
- Materials:
- Ignition-resistant materials, or
- Materials approved for not less than 1-hour fire-resistance-rated construction, or
- 2-inch (51 mm) nominal dimension lumber.
- Protection:
- Fascias are required and shall be protected on the backside by the materials listed above.
- Materials:
Understanding the Code:
Why Protect Eaves and Soffits?
As a wildfire approaches a structure, the heat wave spreads horizontally along the ground and rises, concentrating beneath exterior projections such as eaves and roof overhangs. These areas are particularly vulnerable to ignition because the concentrated heat can easily cause them to catch fire. By protecting the underside of eaves and fascias, we can significantly reduce the risk of fire spreading to the rest of the structure.Materials for Protection:
- Ignition-Resistant Materials: These are materials that have been specifically designed or treated to resist ignition when exposed to flames or intense heat. Examples include certain types of treated wood or composite materials.
- 1-Hour Fire-Resistance-Rated Construction: Materials or assemblies that have been tested and approved to withstand fire exposure for at least one hour. This can include certain types of gypsum board, concrete, or fire-rated wood products.
- Nominal Dimension Lumber: Lumber that meets specific size requirements. The code specifies using 2-inch (51 mm) nominal dimension lumber for its inherent mass and ability to resist ignition. Additionally, 1-inch (25 mm) nominal fire-retardant-treated lumber or 3/4-inch (19.1 mm) nominal fire-retardant-treated plywood can be used. These treated materials must meet the exterior use requirements of Section 2303.2 of the International Building Code, ensuring they are suitable for outdoor conditions and capable of resisting fire.