Is a Specific Type of Separation Required Between a Private Garage and a Dwelling Unit? IBC 406.3.2.1

jar546

CBO
Joined
Oct 16, 2009
Messages
12,983
Location
Not where I really want to be
Do You Agree With The Following Concerning IBC Section 406.3.2.1?

When a private garage is connected to a dwelling unit, including its attic, there must be a separation to ensure a minimum level of protection. This separation must be constructed using gypsum board that is at least 1/2 inch (12.7 mm) thick, applied to the side of the garage.

If the garage is located beneath any habitable space, the separation requirements are more stringent, necessitating the use of 5/8-inch (15.9 mm) Type X gypsum board or a material that offers equivalent protection. Additionally, any structural elements supporting the separation between the garage and the habitable space above must also be protected with a minimum of 1/2-inch (12.7 mm) gypsum board.

For door openings between the garage and the dwelling unit, the doors must be either solid wood or solid or honeycomb core steel doors, each with a minimum thickness of 1 3/8 inches (34.9 mm). Alternatively, doors that comply with Section 716.2.2.1 and have a fire protection rating of at least 20 minutes may be used. All doors must be self-closing and self-latching. It is crucial to note that these doors cannot open directly into a bedroom or any room used for sleeping.

These separation requirements are specifically for private garages and do not apply to carports.
 
Why is a private dwelling unit being looked at under the IBC?

Yes, I know this section is in the IBC, but since the ICC replaced the BOCA code in my state 20 years ago I have yet to see a situation where this applied.
 
Why is a private dwelling unit being looked at under the IBC?

Yes, I know this section is in the IBC, but since the ICC replaced the BOCA code in my state 20 years ago I have yet to see a situation where this applied.
The IBC primarily targets commercial and larger residential buildings, while the IRC covers single-family homes and townhouses. However, some jurisdictions incorporate IBC provisions into their residential codes for added safety, which includes garage separations.

Your state probably sticks to the IRC for residential construction, which might be why you haven’t seen IBC Section 406.3.2.1 in action. Think about some mixed-use applications too.
 
So you have basically paraphrased exactly what the code says (with one exception). Are you asking if you have paraphrased it correctly, or are you asking if we think the requirements are reasonable?

The exception is where you wrote that the door from a private garage cannot open directly into a bedroom or any room used for sleeping. The IBC Commentary says that, but the code doesn't say that, so I don't know where the author(s) of the Commentary came up with that. We can't enforce the Commentary.

If the question is whether or not we think the requirements of IBC 406.3.2.1 are reasonable, my answer is yes.
 
I see that the 2023, 2022 FBC Building does not have the language of openings prohibited 406.3.4.2

2015 IBC

406.3.4.2 Openings Prohibited
Openings from a private garage directly into a room used for sleeping purposes shall not be permitted.

406.3.4.3 Ducts
Ducts in a private garage and ducts penetrating the walls or ceilings separating the dwelling unit from the garage, including its attic area, shall be constructed of sheet steel of not less than 0.019 inch (0.48 mm) in thickness and shall have no openings into the garage.
 
In my area, there are many apartment buildings designed under IBC that are made up of several attached 3-story dwelling units with private garages separated as in these requirements. They look similar to townhouses.
 

Attachments

  • IMG_0380.jpeg
    IMG_0380.jpeg
    1.9 MB · Views: 7
The exception is where you wrote that the door from a private garage cannot open directly into a bedroom or any room used for sleeping. The IBC Commentary says that, but the code doesn't say that, so I don't know where the author(s) of the Commentary came up with that. We can't enforce the Commentary.
2020 La County Building Code based on 2019 CBC and 2018 IBC:

406.2.5 Sleeping rooms. Openings between a motor vehicle-related occupancy and a room used for sleeping purposes shall not be permitted.
 
Regarding the prohibition on openings between a private garage and a sleeping room, it becomes important to verify the language of the code in effect in the jurisdiction, since the model IBC seems to have changed.
 
Regarding the prohibition on openings between a private garage and a sleeping room, it becomes important to verify the language of the code in effect in the jurisdiction, since the model IBC seems to have changed.
Is the omission an error or thought out and done on purpose? Either way you can ignore the lack of a code and do the right thing.
 
Is the omission an error or thought out and done on purpose? Either way you can ignore the lack of a code and do the right thing.

I have no idea if the omission is accidental or intentional. That said, I cannot -- as a code official -- ignore the code and "do the right thing." The right thing for a code official is to enforce the code, as adopted by my jurisdiction. If I attempt to go beyond that, demanding something not required by code because in my infinite wisdom I think it's "the right thing" can get me and the town I work for sued. And since I have no legal authority to demand more than compliance with the code, if I get sued for demanding more than what the code requires, I doubt very much that my qualified immunity would hold up.

One of our former State Building Inspectors often stated in classes: "The code is the least you can accept and the most you can require."

Architects and engineers, of course, can certainly design and specify work that's better than the minimum code requirements. But I can't require them to do so.
 
I have no idea if the omission is accidental or intentional. That said, I cannot -- as a code official -- ignore the code and "do the right thing." The right thing for a code official is to enforce the code, as adopted by my jurisdiction. If I attempt to go beyond that, demanding something not required by code because in my infinite wisdom I think it's "the right thing" can get me and the town I work for sued. And since I have no legal authority to demand more than compliance with the code, if I get sued for demanding more than what the code requires, I doubt very much that my qualified immunity would hold up.

One of our former State Building Inspectors often stated in classes: "The code is the least you can accept and the most you can require."

Architects and engineers, of course, can certainly design and specify work that's better than the minimum code requirements. But I can't require them to do so.
Maybe to allow for efficiency units?
 
That said, I cannot -- as a code official -- ignore the code and "do the right thing."
How do you ignore a code that does not exist? You mention being sued a lot yet I get the idea that you see it as the code and nothing but the code. I on the other hand have been less than a purist. I have invented code and ignored code but unlike you, I have never been sued and have not, nor will I ever, based decisions on the question of a lawsuit.

I do not object to your approach to the job. In fact there have been times when I wish I could follow a narrower path than the one I took. I merely state the differences between us.
 