I have a VB, S-1 occupancy maintenance building. The building itself is 11,400 sqft. I also have an open mezzanine, that will be 550 sqft. And finally, I have a basement level, that is fully exposed on 1 end, and fully underground on the other 3 sides. This is not considered a story based on the Grade Plane Determination Worksheet". The floor area of the basement is 1600 sqft.
Table 506.2, has allowable area of 9000 sqft. In adding frontage increase, per 506.3, I have a new allowable area of 15,570 sqft.
We do not want to sprinkler the building, so we are considering the fire area to be under 12,000 sqft per 903.2.9.
Per IBC 505.2, it states the mezzanine area shall be included in the fire area, so that puts the building above grade, at 11,950 sqft. I have not found anything in the code that states the basement area need to be included in the fire area. I have only found section 506.1.3, that states basements need not to be included in the total allowable floor area of a building.
I have a national post frame builder that is telling me that we need to rate the floor system above the basement, and provide a 3-hr horizontal assembly system per table 707.3.10 to separate the basement and main level, because otherwise the 1600 sqft basement needs to be include in the fire area of the whole project. And we need to do that, because we do not want to sprinkler the building, and adding in the 1600 sqft, puts it over the 12,000 area per ibc 903.2.9
I know is a holiday weekend, but hopefully some people are die-hard works and still working and able to give some insight.
Thanks all. Happy 4th.
Table 506.2, has allowable area of 9000 sqft. In adding frontage increase, per 506.3, I have a new allowable area of 15,570 sqft.
We do not want to sprinkler the building, so we are considering the fire area to be under 12,000 sqft per 903.2.9.
Per IBC 505.2, it states the mezzanine area shall be included in the fire area, so that puts the building above grade, at 11,950 sqft. I have not found anything in the code that states the basement area need to be included in the fire area. I have only found section 506.1.3, that states basements need not to be included in the total allowable floor area of a building.
I have a national post frame builder that is telling me that we need to rate the floor system above the basement, and provide a 3-hr horizontal assembly system per table 707.3.10 to separate the basement and main level, because otherwise the 1600 sqft basement needs to be include in the fire area of the whole project. And we need to do that, because we do not want to sprinkler the building, and adding in the 1600 sqft, puts it over the 12,000 area per ibc 903.2.9
I know is a holiday weekend, but hopefully some people are die-hard works and still working and able to give some insight.
Thanks all. Happy 4th.