Yikes
SAWHORSE
I have a building that per California Fire Code (CFC) Appendix B, table B105.1 would normally require 3,000 GPM fire flow.
However, because the building is sprinklered, this flow rate can be reduced to 1,500 GPM per CFC 105.2.
CFC Appendix C, table C105.1 shows the minimum required number of hydrants, based on required fire flow.
QUESTION: in my example, do I need 3 hydrants because the required flow was 3,000 GPM, or do I only need one hydrant because the reduced flow requirement is only 1,500 GPM?
In other words, is the number of required hydrants based on the reduced flow allowed when a building is sprinklered?
However, because the building is sprinklered, this flow rate can be reduced to 1,500 GPM per CFC 105.2.
CFC Appendix C, table C105.1 shows the minimum required number of hydrants, based on required fire flow.
QUESTION: in my example, do I need 3 hydrants because the required flow was 3,000 GPM, or do I only need one hydrant because the reduced flow requirement is only 1,500 GPM?
In other words, is the number of required hydrants based on the reduced flow allowed when a building is sprinklered?