I disagree with the eliminating sediments traps because of the possibility of pipe shavings, dirt and other debris that may get into the pipe during installation. Now we do not require drips because the local gas company certifies its gas as dry and they are not necessarySediment traps are mostly unnecessary in the vast majority of areas, as NG has gotten much cleaner.
I did not suggest eliminating them and you partially quoted me. See the following that was left off your quote.I disagree with the eliminating sediments traps because of the possibility of pipe shavings, dirt and other debris that may get into the pipe during installation. Now we do not require drips because the local gas company certifies its gas as dry and they are not necessary
IFGC
408.2 Drips.
Where wet gas exists, a drip shall be provided at any point in the line of pipe where condensate could collect. A drip shall also be provided at the outlet of the meter and shall be installed so as to constitute a trap wherein an accumulation of condensate will shut off the flow of gas before the condensate will run back into the meter.
408.3 Location of drips.
Drips shall be provided with ready access to permit cleaning or emptying. A drip shall not be located where the condensate is subject to freezing.
408.4 Sediment trap.
Where a sediment trap is not incorporated as part of the appliance, a sediment trap shall be installed downstream of the appliance shutoff valve as close to the inlet of the appliance as practical. The sediment trap shall be either a tee fitting having a capped nipple of any length installed vertically in the bottommost opening of the tee as illustrated in Figure 408.4 or other device approved as an effective sediment trap. Illuminating appliances, ranges, clothes dryers, decorative vented appliances for installation in vented fireplaces, gas fireplaces, and outdoor grills need not be so equipped.
I was merely sharing information provided to me by our local gas purveyor. As I noted, sediment traps are required per the adopted codes.They are, however are still required.