klarenbeek
REGISTERED
We keep running into the problem of rated IT rooms having non plenum rated wiring in the underfloor plenum. Typically this wiring (or in my current scenario, Sealtite) is ok per the NEC because its an IT room, but as a mechanical only inspector I'm not enforcing the NEC, just the IMC. The IMC does not address IT rooms at all--a plenum is a plenum wherever it is at, so everything in that underfloor IT room plenum has to meet the same requirements of any other plenum. Just wondering if anyone else was running into the same issues or how you were addressing this situation. Thanks.