• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Kind if a mixed elevator question

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
Saw this on another forum

And just wonder,

A. Has anyone seen some of this set ups?

B. anyone enforce some of the not in the book stuff

C. Any references to some of the stuff that does not sound like it is in the book

""""

Please be aware that starting the mid 90s elevators in fully auto sprinklered buildings were constructed with a circuit that electricians call a "shunt trip." The circuit gets it's name from the characteristic that it "shunts", or redirects, some of the current from the circuit breaker supplying power to the elevator circuits to a solenoid located inside the breakers case. That solenoid trips the breaker to the open position. The purpose of the circuit is to insure that the elevator machinery will be de-energized prior to the discharge of water from automatic sprinklers that are located in elevator shafts and machine rooms. Let me emphasize that none of this is effected by what mode of service the elevator is in. In can be under automatic, local control, inspection, and, yes even, fire service control and the shunt trip circuit will still operate. If this should occur while firefighters are in the elevator cab; and that cab is not at a floor landing with it's door open; then the elevator cab becomes a coffin on a tube or a coffin on cables.

The circuit is initiated by heat detectors that are located adjacent to the sprinkler heads located in elevator shafts and machine rooms. The detectors are selected to operate at a lower temperature than the temperature at which the sprinkler head will open and discharge water. Once the shunt trip solenoid is energized there is no way to restore power to the elevator equipment. Any attempt to re-close the circuit breaker will re-energize the solenoid and trip the breaker to the open position immediately.

For the first six years of the rule's application there was no requirement to integrate that circuit with the elevator's fire alarm recall system. The earliest version of this circuit provided no warning of any kind prior to the operation of the circuit. When one of the heat detectors operates all power to the elevators is lost. Thousands of elevators were constructed under that first version of the shunt trip rule.

The second version of the rule required that the circuit had to include delayed operation and a warning light located in the cab. The warning light is often inscrutably labeled "Shunt Trip" The label may not be visible until the warning light comes on. Once that warning light illuminates you have only a brief time prior to the operation of the shunt trip circuit. The required delay was one minute. There was still no integration with the elevator controls. If you use an elevator that was constructed under this second version of the rule the safety of everyone in the cab will depend of someone knowing which light to monitor and their stopping of the elevator immediately at the next floor of travel so that everyone can leave the cab. In all but the fastest elevators you may not have time to return to the floor from which you entered the cab.

Later versions of the rule required that these circuits be integrated with the elevator controls and automatically return the elevator to it's primary or alternate floor before shutting down all power to the elevator equipment. Although that avoids trapping firefighters in the elevator cab it can leave the initial attack team isolated several stories above the street with no backup, RIT, or any help whatsoever. In the event a firefighter or civilian has to be evacuated it will not be possible to use the elevator to do so."""
 