1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Kitchen grinder(disposal) to grease trap

Discussion in 'Commercial Plumbing Codes' started by chris kennedy, Aug 31, 2018.

  1. chris kennedy

    chris kennedy Sawhorse

    Joined:
    Oct 24, 2009
    Messages:
    1,283
    Likes Received:
    57
    Doing a commercial kitchen and today the plumbers failed an inspection due to the fact the grinder was draining through the grease trap. Inspector said it had to go to sanitary.

    Anyone have a code reference to back this up? Inspector didn't site code.

    Thanks
     
  2. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,061
    Likes Received:
    406
    IPC (2012) 1003.3.2 where food waste grinders connect to grease interceptor a solids interceptor shall separate the discharge before the grease interceptor.

    And of course your AHJ may have amended this section or a memorandum of agreement with public works that differ.
     
  3. Flexo

    Flexo Registered User

    Joined:
    Jan 28, 2018
    Messages:
    18
    Likes Received:
    3
    The 2012 IPC "1003.3.2 Food Waste Grinders. Where solid waste grinders connect to grease interceptors, a solids interceptor shall separate the discharge before connecting to the grease interceptor. Solids interceptors and grease interceptors shall be sized and rated for the discharge of the food waste grinder. Emulsifiers, chemicals,enzymes and bacteria shall not discharge into the food waste grinder."
     
  4. chris kennedy

    chris kennedy Sawhorse

    Joined:
    Oct 24, 2009
    Messages:
    1,283
    Likes Received:
    57
  5. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,484
    Likes Received:
    210
  6. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,877
    Likes Received:
    34
    Problem is that these small grease traps don't do the job and the code is way behind.
     
  7. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,746
    Likes Received:
    543
    IPC allows it to go to the grease interceptor with a solids separator. The UPC does not unless approved by the AHJ

    UPC 1014.1.3
    Unless specifically required or permitted by the AHJ no food disposal unit or dishwasher shall be connected to or discharge into a grease interceptor. Commercial food waste disposer shall be permitted to discharge directly into the buildings drainage system.
     
    Pcinspector1 likes this.
  8. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,394
    Likes Received:
    225
    Good inspector, knows his stuff!

    You don't want the bathroom toilet paper and what ever the public flushes going into that GT either!
     
  9. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    719
    Likes Received:
    10
    Was the grease trap sized for the volumetric flow rate of the pump plus the kitchen fixtures?
     