• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Kitchenette in clubhouse for R2

Everything.... the sink, range, exhaust fan, fridge, work surface, outlets, etc.

Always remember that the IBC provides the scoping, A117.1 tells you how (at least for most of us who do not administer the ADA).

1109.4 Kitchens and Kitchenettes
Where kitchens and kitchenettes are provided in accessible spaces or rooms, they shall be accessible.
As per A117.1, you will need the following:
  • An accessible work surface shall be provided with a minimum width of 30-inches and maximum height of 34-inches (804.3);
  • With a cook top, a roll-under type kitchenette sink is required (804.4 and 606.2);
  • Cooktop controls shall not require reaching across burners (804.5.4.4);
  • Range hood controls shall be within the accessible reach range (804.5.2 and 309);
  • Refrigerator/Freezers shall have at minimum 50% of compartment shelves 54-inches maximum above the floor (804.5.6).


 