• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Landing at Accessibility Lift

Mech

Registered User
Joined
Oct 30, 2009
Messages
1,037
Location
Eastern PA
2018 IBC

Existing building

Owner is looking to add a vertical chair lift from to provide accessibility to the basement from exterior grade. A 65 sf addition (shown in blue) will enclose the lift.

1709664795087.png



The proposed exterior door is 30"x70"; I am not sure how they arrived at this size. If the chair lift is not a code compliant means of egress, must the door meet the code minimum size?


Must I provide a landing on each side of the exterior door? The exterior side has ample width and depth.

1709662996738.png

Thanks in advance.
 
A 30" x 70" door provides a clear opening width of 27" (approximately). A117.1 and the ADA require 32" clear with the door open 90 degrees, which rquires a 35" door unless the hinges are offset hinges.
 