I wanted to gain insight from fellow Canadians on the application of Part 9 to large truss span buildings.
I had a plan come across my desk today that had a portion of a house with a clear span of 48 feet (14.63m). This clearly exceeds the 12.2 metre threshold set in 9.23.1.1(1)(e).
I've requested the client either provide evidence of mid-range support for the truss, or gain engineer design for the wall supporting this element. I'm also cognizant of 9.4.2.1(c), in relation to snow loads.
Wall is a standard 2x6 @ 16" (40cm) centres. An engineer has designed - but not stamped - the plans, so this ought not to be a great challenge, but I wanted to gain a second opinion on whether I'm interpreting 9.23.1.1 correctly. I found the note and the illustrated guide particularly unhelpful.
I had a plan come across my desk today that had a portion of a house with a clear span of 48 feet (14.63m). This clearly exceeds the 12.2 metre threshold set in 9.23.1.1(1)(e).
I've requested the client either provide evidence of mid-range support for the truss, or gain engineer design for the wall supporting this element. I'm also cognizant of 9.4.2.1(c), in relation to snow loads.
Wall is a standard 2x6 @ 16" (40cm) centres. An engineer has designed - but not stamped - the plans, so this ought not to be a great challenge, but I wanted to gain a second opinion on whether I'm interpreting 9.23.1.1 correctly. I found the note and the illustrated guide particularly unhelpful.