2012 IBC, Type II-B Construction

I received a comment from my plan reviewer regarding built-in wood benches in a restaurant, stating that I need to show that the amount of wood benches is under the limit allowed for combustible materials. Where would I find this limit stated in the code? And is it the IBC or International Fire Code, or other?
 
I believe it is in chapter 8, interior finishes don't have my book in front of me at the moment.
Section 805 does refer to combustible materials in types I and II construction, but it doesn't talk about anything like built-in benches. Just subfloors, wood flooring and insulating boards.
 
If you were to reach and call the benches combustible trim........I think I would have a hard time going there.


[F] 806.7 Interior trim. Material, other than foam plastic

used as interior trim, shall have a minimum Class C flame

spread and smoke-developed index when tested in accordance

with ASTM E84 or UL 723, as described in Section

803.1.1. Combustible trim, excluding handrails and guardrails,

shall not exceed 10 percent of the specific wall or ceiling

area to which it is attached.
 
It is furniture, built onsite or brought in and bolted into place the combustible loading is the same. Sheet rock the walls and build the furniture or hang the wood cabinets Make him provide the code section to prove you are wrong.
 
Guess I need to ask about wood table chairs now.

Small town? To much time?

Yes ask for the code reference
 
Perhaps the plan checker is referencing 2 provisions that mentions furnishing. (2012) Table 803.9 Note f. "chancel furnishing" is exempt and Section 806; "Fixed or movable walls and partitions, paneling, wall pads and crash pads applied structurally or for decoration, acoustical correction, surface insulation or other purposes shall be considered interior finish if they cover 10 percent or more of the wall or of the ceiling area, and shall not be considered decorative materials or furnishings.

The 2018 Section 801.1 "The provisions of this chapter shall govern interior finish, interior trim, furniture, furnishings, decorative materials and decorative vegetation in buildings. Existing building shall comply with Sections 803 through 808. New buildings shall comply with Section s 804 through 808, and Section 803 of the IBC."

Lots of new sections in the 2018 Chapter 8 that further clarify and expands on combustibles in certain use groups.
 
Guess I need to ask about wood table chairs now.

Small town? To much time?

Yes ask for the code reference
Yes, small town. Maybe too much time. I'll ask for specific code section. Thanks, all!
 
My 2018 does not have the words "furniture or furnishings" in the scope

CHAPTER 8
INTERIOR FINISHES


User notes:
About this chapter: Chapter 8 contains the performance requirements for controlling fire growth and smoke propagation within buildings by restricting interior finish and decorative materials. The provisions of this chapter require materials used as interior finishes and decorations to meet certain flame spread index or flame propagation criteria and smoke development criteria based on the relative fire hazard associated with the occupancy. The performance of the material is evaluated based on test standards.
Code development reminder: Code change proposals to sections preceded by the designation [F] will be considered by the International Fire Code Development Committee during the 2019 (Group B) Code Development Cycle.


SECTION 801
SCOPE

801.1 Scope.
The provisions of this chapter shall govern the use of materials used as interior finishes, trim and decorative materials

806 does use the word furnishings

SECTION 806
DECORATIVE MATERIALS AND TRIM

[F] 806.1 General.
The following requirements shall apply to all occupancies:

1. Furnishings or decorative materials of an explosive or highly flammable character shall not be used.

2. Fire-retardant coatings in existing buildings shall be maintained so as to retain the effectiveness of the treatment under service conditions encountered in actual use.

3. Furnishings or other objects shall not be placed to obstruct exits, access thereto, egress therefrom or visibility thereof.

4. The permissible amount of decorative vegetation and noncombustible decorative materials shall not be limited.
 
FV, read Section 801.1 that you posted—it does state “furniture, furnishings...”
 
2012 IBC, Type II-B Construction

I received a comment from my plan reviewer regarding built-in wood benches in a restaurant, stating that I need to show that the amount of wood benches is under the limit allowed for combustible materials. Where would I find this limit stated in the code? And is it the IBC or International Fire Code, or other?

Our fire marshal reviews all commercial plans, as does planing & zoning, infrastructure, ect.
 
FV
Section 805 of the 2018 IFC deals with upholstered furniture in specific I, R and B ambulatory care facilities. "A" occupancies are not mentioned.

I see it as an enforcement nightmare because we final buildings all the time with no furniture in them.
 
The Fire Safety reviewer for state buildings in Virginia has required us to fill concealed combustible spaces within fixed benches with fiberglass insulation or else provide sprinklers in them.
 
The Fire Safety reviewer for state buildings in Virginia has required us to fill concealed combustible spaces within fixed benches with fiberglass insulation or else provide sprinklers in them.


Sounds like they are using the “ code stretcher 3000” 2016 year model
 