I have a local design professional proposing a LAS in a new stand alone crematorium building for a local funeral home. 1200 sq. feet and we're on 2012 I-codes. The design professional originally intended to sprinkler only the room with the cremator/incinerator in it and provide the appropriate separation between it and the viewing room. Given the small size of the building he is now proposing to sprinkler the entire building because he thinks he can do it and stay under the 20 head threshold.
The domestic supply has to be able to supply the system and the domestic demand simultaneously. The only demand I can see is a hand sink and two single user toilet rooms. My concern is that it looks like the 2015 IFC is moving towards a more restrictive approach to the limited area systems. 6 heads and light hazard or ordinary hazard-group 1 classifications only.
So to make a short story long, what hazard classification would be appropriate for the crematorium in this scenario? Can the required design density for this hazard classification be supplied? It looks like that is the concern that is driving the more restrictive language in the 2015 IFC. Am I overthinking this? The fire load is really just the body and the equipment in the space, correct? Is a light hazard classification appropriate. They do have an overhead door that allows them to pull a vehicle in to unload the body.
The domestic supply has to be able to supply the system and the domestic demand simultaneously. The only demand I can see is a hand sink and two single user toilet rooms. My concern is that it looks like the 2015 IFC is moving towards a more restrictive approach to the limited area systems. 6 heads and light hazard or ordinary hazard-group 1 classifications only.
So to make a short story long, what hazard classification would be appropriate for the crematorium in this scenario? Can the required design density for this hazard classification be supplied? It looks like that is the concern that is driving the more restrictive language in the 2015 IFC. Am I overthinking this? The fire load is really just the body and the equipment in the space, correct? Is a light hazard classification appropriate. They do have an overhead door that allows them to pull a vehicle in to unload the body.