Linen closet requirements

SCBO1

REGISTERED
Joined
Oct 28, 2009
Messages
4,610
Location
MID WEST
I'm looking for linen closet construction requirements, I thought there was some requirements like a 1-HR wall requirement and or a sprinkler requirement? Code section?

pc1
 
Pcinspector,

Are you possibly referring to "Incidental Storage Areas"?

TABLE 508.2 INCIDENTAL USE AREAS

ROOM OR AREA

SEPARATION AND/OR PROTECTION

Furnace room where any piece of equipment is over 400,000 Btu per hour input

1 hour or provide automatic fire-extinguishing system

Rooms with boilers where the largest piece of equipment is over 15 psi and 10 horsepower

1 hour or provide automatic fire-extinguishing system

Refrigerant machinery rooms

1 hour or provide automatic sprinkler system

Parking garage (:Next('./icod_ibc_2006f2_4_sec006_par005.htm')'>Section 406.2)

2 hours; or 1 hour and provide automatic fire-extinguishing system

Hydrogen cut-off rooms, not classified as Group H

1-hour in Group B, F, M, S and U occupancies. 2-hour in Group A, E, I and R occupancies.

Incinerator rooms

2 hours and automatic sprinkler system

Paint shops, not classified as Group H, located in occupancies other than Group F

2 hours; or 1 hour and provide automatic fire-extinguishing system

Laboratories and vocational shops, not classified as Group H, located in Group E or I-2 occupancies

1 hour or provide automatic fire-extinguishing system

Laundry rooms over 100 square feet

1 hour or provide automatic fire-extinguishing system

Storage rooms over 100 square feet

1 hour or provide automatic fire-extinguishing system

Group I-3 cells equipped with padded surfaces

1 hour

Group I-2 waste and linen collection rooms

1 hour

Waste and linen collection rooms over 100 square feet

1 hour or provide automatic fire-extinguishing system

Stationary storage battery systems having a liquid capacity of more than 100 gallons used for facility standby power, emergency power or uninterrupted power supplies

1-hour in Group B, F, M, S and U occupancies. 2-hour in Group A, E, I and R occupancies.

.
 
Last edited by a moderator:
Globe,

Just wanted to make sure I did'nt miss something, the plans appear to be compliant, closets not rooms. I thought I had seen something on linen closets but could not find it!

Under the square footage requirement.

Thanks

pc1
 
Globe,

52 s.f. with one pendent sprinkler, 5/8" fire shield, mold resistant drywall. I think its good to go.

pc1
 