4.12.2 Equipment Access. Fire pump rooms should be accessible under fire conditions. Where a fire pump room cannot be located on grade with direct access from outside of the building, a protected space with a fire rating in accordance with Table 4.12.1.1.2 must be provided. The space must be accessible through an enclosed passageway from an exterior exit or from an enclosed stairway.4.12.2.1 The location of and access to the fire pump room(s) shall be pre-planned with the fire department.
4.12.2.1.1 Fire pump rooms not directly accessible from the outside shall be accessible through an enclosed passageway from an enclosed stairway or exterior exit.
4.12.2.1.2 The enclosed passageway shall have a fire-resistance rating not less than the fire-resistance rating of the fire pump room. NFPA 20, 2013