Per the stairwell reentry requirements, if stair doors are locked on the stair side, they need to be able to be unlocked via the fire alarm or fire command center to allow someone to leave the stair and find another exit. The egress side needs to be unlocked at all times to allow access to the stair. There is an exception (#1) for the stair discharge door, which has to be unlocked on the stair side but can be locked on the opposite side. The question has come up regarding the attached partial plan, whether it's acceptable per the IBC to lock the corridor side of the door swinging out of the stairs. The stair side allows free egress to the corridor. There is an identical stair, stair discharge door, and exterior door at the other end of the corridor, with no locked doors in between. The corridor side of the stair door does not unlock on fire alarm or a signal from the fire command center.I think it's acceptable to lock the corridor side of the stair discharge door, but I've been asked to confirm, so what say you?Here's the partial plan: View attachment 1471Here's the IBC 2009 text in case you want to review it:1008.1.9.10 Stairway doors. Interior stairway means of egress doors shall be openable from both sides without the use of a key or special knowledge or effort. Exceptions: 1. Stairway discharge doors shall be openable from the egress side and shall only be locked from the opposite side.2. This section shall not apply to doors arranged in accordance with Section 403.12.3. In stairways serving not more than four stories, doors are permitted to be locked from the side opposite the egress side, provided they are openable from the egress side and capable of being unlocked simultaneously without unlatching upon a signal from the fire command center, if present, or a signal by emergency personnel from a single location inside the main entrance to the building.
View attachment 1727
View attachment 1727
/monthly_2012_10/572953e709edc_StairPartialPlan.jpg.89dd74a6f42ced1fd004ab7a71f61c06.jpg
View attachment 1727
View attachment 1727
/monthly_2012_10/572953e709edc_StairPartialPlan.jpg.89dd74a6f42ced1fd004ab7a71f61c06.jpg