Sifu
SAWHORSE
- Joined
- Sep 3, 2011
- Messages
- 3,459
A proposal for am A-2/A3 has come in. Within the space is a storage/mech. room. However within the room are employee lockers. It is largely an employee workspace for storage and equipment such as the water heater, CO2 tanks, and soda racks, but with a bank of employee lockers, ergo it is a room, with lockers. I see no way around the fact that at least 5% of the lockers must be accessible per 2018 IBC 1109.9. But would it be considered a "locker room" in the context of ANSI 117.1 803? The issue is that the room does not allow room for the bench required by ANSI 803/903 without some reconfiguration. Happy to cite that requirement, just want to be sure of the distinction between a locker being accessible vs. a designated "locker room".