Francis Vineyard
REGISTERED
Does anyone know what happended to Section R101.5.2 in the 2015 IECC?
http://codes.iccsafe.org/app/book/content/2015-I-Codes/2015%20IECC%20HTML/Chapter%201%20[RE].html
2012 IECC;
R101.5 Compliance.
Residential buildings shall meet the provisions of IECC—Residential Provisions. Commercial buildings shall meet the provisions of IECC—Commercial Provisions.
R101.5.1 Compliance materials.
The code official shall be permitted to approve specific computer software, worksheets, compliance manuals and other similar materials that meet the intent of this code.
R101.5.2 Low energy buildings.
The following buildings, or portions thereof, separated from the remainder of the building by building thermal envelope assemblies complying with this code shall be exempt from the building thermal envelope provisions of this code:
1. Those with a peak design rate of energy usage less than 3.4 Btu/h • ft2 (10.7 W/m2) or 1.0 watt/ft2 (10.7 W/m2) of floor area for space conditioning purposes.
2. Those that do not contain conditioned space.
http://codes.iccsafe.org/app/book/content/2015-I-Codes/2015%20IECC%20HTML/Chapter%201%20[RE].html
2012 IECC;
R101.5 Compliance.
Residential buildings shall meet the provisions of IECC—Residential Provisions. Commercial buildings shall meet the provisions of IECC—Commercial Provisions.
R101.5.1 Compliance materials.
The code official shall be permitted to approve specific computer software, worksheets, compliance manuals and other similar materials that meet the intent of this code.
R101.5.2 Low energy buildings.
The following buildings, or portions thereof, separated from the remainder of the building by building thermal envelope assemblies complying with this code shall be exempt from the building thermal envelope provisions of this code:
1. Those with a peak design rate of energy usage less than 3.4 Btu/h • ft2 (10.7 W/m2) or 1.0 watt/ft2 (10.7 W/m2) of floor area for space conditioning purposes.
2. Those that do not contain conditioned space.