JBI,
I got to thinking some more about your office conversation.
Assuming the LP gas line your are referring to is plastic, an
electrical tracer line is required to be installed
[ RE: Section 404.17.3, `12 IFGC ]........If the gas line is
installed in the same trench with electrical conduit, detection
of the 2 individual systems could be \ might be a problem.
I have asked some colleagues about installing 2 types of utilities
in to one trench.....The concensus is that it is not good practice,
nor would it be meeting the intent of Section 101.3 - Intent
[ `12 IBC ] in establishing the "minimum" requirements to
safeguard the public health, safety and general welfare through
safety to life and property from fire and other hazards.
While the various codes do not address every single application
out in the built environment, ...I believe that Section 101.3
allows the Code Official to make a determination of what they
deem safe and unsafe.........Some may agree while others may
disagree.......Essentially, it would be an AHJ call.
If it were my call to make, I would say No, ...do not install in the
same trench, unless there is adequate separation and
identification between the systems being installed.
Hope this helps !
~ # ~ # ~