magnetic locks
cda
Basement
so front door of a B occupancy. one exit only, no fire sprinkler system, no fire alarm system
2009 IBC
1. Has a magnetic lock on the door
2. Has a electronic touch bar on the door, to release the magnetic lock
no other hardware or electronics
so does; this apply with no other requirements?
1008.1.9.8 Electromagnetically locked egress doors. Doors in the means of egress that are not otherwise required to have panic hardware in buildings with an occupancy in Group A, B, E, M, R-1 or R-2 and doors to tenant spaces in Group A, B, E, M, R-1 or R-2 shall be permitted to be electromagnetically locked if equipped with listed hardware that incorporates a built-in switch and meet the requirements below:1. The listed hardware that is affixed to the door leaf has an obvious method of operation that is readily operated under all lighting conditions.2. The listed hardware is capable of being operated with one hand.3. Operation of the listed hardware releases to the electromagnetic lock and unlocks the door immediately.4. Loss of power to the listed hardware automatically unlocks the door.
OR does this apply or some other section??:::
1008.1.4.4 Access-controlled egress doors. The entrance doors in a means of egress in buildings with an occupancy in Group A, B, E, I-2, M, R-1 or R-2 and entrance doors to tenant spaces in occupancies in Groups A, B, E, I-2, M, R-1 and R-2 are permitted to be equipped with an approved entrance and egress access control system which shall be installed in accordance with all of the following criteria:1. A sensor shall be provided on the egress side arranged to detect an occupant approaching the doors. The doors shall be arranged to unlock by a signal from or loss of power to the sensor.2. Loss of power to that part of the access control system which locks the doors shall automatically unlock the doors.3. The doors shall be arranged to unlock from a manual unlocking device located 40 inches to 48 inches (1016 mm to 1219 mm) vertically above the floor and within 5 feet (1524 mm) of the secured doors. Ready access shall be provided to the manual unlocking device and the device shall be clearly identified by a sign that reads "PUSH TO EXIT." When operated, the manual unlocking device shall result in direct interruption of power to the lock-independent of the access control system electronics-and the doors shall remain unlocked for a minimum of 30 seconds.4. Activation of the building fire alarm system, if provided, shall automatically unlock the doors, and the doors shall remain unlocked until the fire alarm system has been reset.5. Activation of the building automatic sprinkler or fire detection system, if provided, shall automatically unlock the doors. The doors shall remain unlocked until the fire alarm system has been reset.6. Entrance doors in buildings with an occupancy in Group A, B, E or M shall not be secured from the egress side during periods that the building is open to the general public.
they are not doing this on the egress side:::
"""Doors can be protected by controlled egress or free egress. A controlled egress door requires permission from the access control system to allow someone to enter or exit through the door. This type is used where entry and exit must be logged or where areas on both sides of the passage must be controlled. An entrance door that was locked or controlled from the exterior, but allowed free egress at any time, such as with a panic bar or other standard hardware, would not be an access controlled egress door. This locking arrangement is for situations where both the ingress and egress out of the door is controlled by some type of entry system, such as a key pad or card swipe. """"
no card reader or fob to get out.