508.1.1 Makeup Air Temperature
The temperature differential between makeup air and the air in the conditioned space shall not exceed 10°F (6°C) except where the added heating and cooling loads of the makeup air do not exceed the capacity of the HVAC system.
Hi, I'm looking for some help w/ this requirement. How can I prove that the existing a/c system is capable of handling the added commercial hood kitchen ventilation? We're installing a small hood 4'x8' in a little more than 2,000 sf convenient store of a gas station. So the exhaust is 3,200 cfm, and the make-up air is 2,800 cfm. Two 5-ton roof top a/c units is capable of handling this added load, but I'm having trouble of proving it. If anybody has the answer or good suggestion, please let me know. Thanks a lot.
The temperature differential between makeup air and the air in the conditioned space shall not exceed 10°F (6°C) except where the added heating and cooling loads of the makeup air do not exceed the capacity of the HVAC system.
Hi, I'm looking for some help w/ this requirement. How can I prove that the existing a/c system is capable of handling the added commercial hood kitchen ventilation? We're installing a small hood 4'x8' in a little more than 2,000 sf convenient store of a gas station. So the exhaust is 3,200 cfm, and the make-up air is 2,800 cfm. Two 5-ton roof top a/c units is capable of handling this added load, but I'm having trouble of proving it. If anybody has the answer or good suggestion, please let me know. Thanks a lot.