• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Maneuvering clearance at automatic door

kasa

Member
Joined
Apr 13, 2012
Messages
46
I've got an existing building with a manual front main entrance door, which is lacking the required 18" clearance (seen in table 404.2.3.2, ICC A117.1-2009) for front approach from pull side. In considering installing an automatic door, I see 404.3.2 requiring them to return to section 404.2.3 for maneuvering clearances. Since table 404.2.3.2 specifies it's for manual swinging doors, does this mean the automatic door here doesn't need the 18" clearance? For the control switch, it says it must be 'beyond the arc of the door swing', is there any other location requirements, aside from the usual reach areas for a button?
 
It depends on the type of automatic door. Power-assisted doors are still required to comply with the clearances. Power-assisted doors are those that still require manual operation, but make it easier to do so by reducing the needed force to put them in motion. Automatic doors, like those at many grocery stores, are full-powered doors and automatically open based on a motion sensor or stepping on a control mat. Those types of doors do not require the minimum clear space at the door (but require railings to prevent people from getting smacked in the face by a door). The type I think you are considering is what is referred to as a low-energy door. Low-energy doors have an operator that will open the door once a button or plate is pushed, but can also be opened manually. These doors also are not required to provide the minimum clear space at the door, but a 30" by 48" clear space at the button/plate is required and it must be outside the swing of the door.
 
404.3.4 requires automatic door operators to have backup power to be exempt from maneuvering clearances.
That would be Section 404.3.2 per the ADA Standards--there is no mention of it in the 2009 ANSI A117.1. The ADA standards do not define "standby power," so this could be a typical battery back-up system.
 