It is word for word in the IEBC however the IEBC includes R-2 and R-3 occupancies
505.3 Replacement window emergency escape and rescue openings.
Where windows are required to provide emergency escape and rescue openings in Group R-2 and R-3 occupancies and one- and two-family dwellings and townhouses regulated by the International Residential Code, replacement windows shall be exempt from the requirements of Sections 1030.2, 1030.3 and 1030.4 of the International Building Code and Sections R310.2.1, R310.2.2 and R310.2.3 of the International Residential Code, provided that the replacement window meets the following conditions:
1. The replacement window is the manufacturer’s largest standard size window that will fit within the existing frame or existing rough opening. The replacement window shall be permitted to be of the same operating style as the existing window or a style that provides for an equal or greater window opening area than the existing window.
2. The replacement of the window is not part of a change of occupancy.
Window opening control devices complying with ASTM F2090 shall be permitted for use on windows required to provide emergency escape and rescue openings.
And another IEBC section with no mention of sill height maximum
1011.4.1 Means of egress for change to a higher-hazard category.
Where a change of occupancy classification is made to a higher-hazard category (lower number) as shown in Table 1011.4, the means of egress shall comply with the requirements of Chapter 10 of the International Building Code.
Exceptions:
7. An existing operable window with clear opening area
not less than 4 square feet (0.38 m2) and minimum opening height and width of 22 inches (559 mm) and 20 inches (508 mm), respectively,
shall be accepted as an emergency escape and rescue opening.