I agree and that is out of the IBC which may apply if the language is not in the IRC and this is a residential question. I am assuming this is a loading question and not a span question although the two are inter-related.steveray said:I would have no problem limiting them to 40' I imagine......SECTION 2308 CONVENTIONAL LIGHT-FRAME CONSTRUCTION
2308.1 General.
The requirements of this section are intended for conventional light-frame construction. Other methods are permitted to be used provided a satisfactory design is submitted showing compliance with other provisions of this code. Interior nonload-bearing partitions, ceilings and curtain walls of conventional light-frame construction are not subject to the limitations of this section. Alternatively, compliance with the following standard shall be permitted subject to the limitations therein and the limitations of this code: American Forest and Paper Association (AF&PA) Wood Frame Construction Manual for One- and Two-Family Dwellings (WFCM).
5. Roof trusses and rafters shall not span more than 40 feet (12 192 mm) between points of vertical support.
mtlogcabin said:Truss roof framing constructed in accordance with the provisions of this section shall be limited to sites subjected to a maximum design wind speed of 110 miles per hour (49 m/s), Exposure A, B or C, and a maximum ground snow load of 70 psf (3352 Pa).Unless you are in a high wind and over 70 psf ground snow then trusses designed under ANSI/TPI 1 are not limited in size.
Don't try and use the IBC to disallow what is specifically permitted in the prescriptive IRC code
There are similar restrictions for steel trusses and SIPs panel construction, R603.1.1 & R613.2
Agree and in my seismic zone it is easy to require an engineer on an irregular shaped building.The fact of the matter is people are building way more advanced homes than they know how to....And as long as there are gray ares in the code, if there is something I am not comfortable with, I will have no issues sending someone to a (hopefully competent and ethical) design professional.....