MC question

SCBO1

REGISTERED
Joined
Oct 28, 2009
Messages
4,647
Location
MID WEST
Is MC cable considered to be electrical metallic tubing? Would it require stud guards if placed to close to the edge of a stud?

NEC 300.4 A,1
 
330.17 Through or Parallel to Framing Members. Type MC cable shall be protected in accordance with 300.4(A), ©, and (D) where installed through or parallel to framing members.
 
Gregg, thanks, I thought I was correct requiring the guards, their always working on me.

pc1
 
As a point of clarity, would the nail guards be required for MC cable if installed

in metal framing? Yes, no? Article or code sections please!

Thanks!

.
 