Means of Egress Headroom Requirements

jar546

CBO
Joined
Oct 16, 2009
Messages
12,763
Location
Not where I really want to be

Some Changes in the 2023 FBC should coincide with the IBC. Exception addes.

1003.3.1 Headroom.​

Protruding objects are permitted to extend below the minimum ceiling height required by Section 1003.2 where a minimum headroom of 80 inches (2032 mm) is provided over any walking surface, including walks, corridors, aisles and passageways. Not more than 50 percent of the ceiling area of a means of egress shall be reduced in height by protruding objects.

Exception: Door closers, overhead door stops, frame stops, power door operators and electromagnetic door locks shall be permitted to project into the opening height not lower than 78 inches (1981 mm).

A barrier shall be provided where the vertical clearance is less than 80 inches (2032 mm) high. The leading edge of such a barrier shall be located 27 inches (686 mm) maximum above the floor.
 
I wonder how that works with this (exception) from 2021 IBC, which I've used a number of times for orchestra pits:

1208.2 Minimum ceiling heights.

Occupiable spaces, habitable spaces and corridors shall have a ceiling height of not less than 7 feet 6 inches (2286 mm) above the finished floor. Bathrooms, toilet rooms, kitchens, storage rooms and laundry rooms shall have a ceiling height of not less than 7 feet (2134 mm) above the finished floor.

Exceptions:

2. If any room in a building has a sloped ceiling, the prescribed ceiling height for the room is required in one-half the area thereof. Any portion of the room measuring less than 5 feet (1524 mm) from the finished floor to the ceiling shall not be included in any computation of the minimum area thereof.
 