I am working on mechanical design for a salon that is 1955 net sf. 2103 gross sf.
Main Salon area 1843 SF
Restroom 56 SF
Restroom 56 SF
According to NC Building Code occupant load (Business= 100gross), occupant load is 2103/100= 22 occupants.
According to NC Mechanical Code 403.3.1.1, Occupant density for salon is 25/1000sf. 25/1000= .025*1843= 46 occupants.
Does anyone know why the Mech code boosts the occupant load?
For life safety/ actual max occupancy one would go with the Building Code way to calculate occupancy.
Why does Mech code calculation result in more than double occupancy? If you use Mech Code way to calculate occupancy for HVAC loads, then that greatly increases your O.A. requirements, which in turn increases your overall HVAC requirements.
Seems to me it makes more sense to calculate the occupancy based on the ACTUAL max occupancy as given by the Building code.
Anyone else run into this issue?
Thanks
Michael
Main Salon area 1843 SF
Restroom 56 SF
Restroom 56 SF
According to NC Building Code occupant load (Business= 100gross), occupant load is 2103/100= 22 occupants.
According to NC Mechanical Code 403.3.1.1, Occupant density for salon is 25/1000sf. 25/1000= .025*1843= 46 occupants.
Does anyone know why the Mech code boosts the occupant load?
For life safety/ actual max occupancy one would go with the Building Code way to calculate occupancy.
Why does Mech code calculation result in more than double occupancy? If you use Mech Code way to calculate occupancy for HVAC loads, then that greatly increases your O.A. requirements, which in turn increases your overall HVAC requirements.
Seems to me it makes more sense to calculate the occupancy based on the ACTUAL max occupancy as given by the Building code.
Anyone else run into this issue?
Thanks
Michael