I've got a fire smoke damper with control voltage of 120V (Life Safety Branch - in a hospital) which is controlled via a fire alarm control module in a fail safe manner. i.e. if the power fails, the damper closes. Our spec calls for all Emergency wiring to be mechanically protected in accordance with 517.30©(3) and so the contractor provided the 120V power to the unit in pipe but did not wire the control wiring from the CM module in pipe.
I think this is ok but the owner is questioning it. The reason I think it's ok is that a) the control via the CM is a continuation of the Fire Alarm system which does not need to be in conduit and b) from a practical standpoint, the system is fail safe, if the wiring is damaged for whatever reason, the damper closes. Do you think this reasoning sound? Am I missing something either in my argument for it or forming the foundation for an argument against?
I much appreciate your feedback,
Mike
I think this is ok but the owner is questioning it. The reason I think it's ok is that a) the control via the CM is a continuation of the Fire Alarm system which does not need to be in conduit and b) from a practical standpoint, the system is fail safe, if the wiring is damaged for whatever reason, the damper closes. Do you think this reasoning sound? Am I missing something either in my argument for it or forming the foundation for an argument against?