1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Medical Procedure Room

Discussion in 'Mechanical Codes' started by rgrace, Oct 30, 2019.

  1. rgrace

    rgrace Sawhorse

    Joined:
    Feb 18, 2010
    Messages:
    184
    Likes Received:
    46
    The 2015 IMC completely removed the occupancy classification of "Hospitals, nursing and convalescent homes" and its sub-catigories from Table 403.3. At the same time, Section 407 was added for ambulatory care facilities and Group I-2 occupancies, which sends you to ASHRAE 170. This is consistant in the 2018 and 2021 editions of IMC.

    What ventilation rates do you now use for medical procedure rooms (biopsy, exam rooms, dental, infusion centers, etc) or physical therapy rooms that are all classified Group B? IMC 403.3.1.1 says to pick ventilation rates that are most similar in terms of occupant density, activities and building construction; or approved engineering analysis (which I try to avoid). Do you go back one cycle? Do you go to ASHRAE 170? Do you choose a similar occupancy classification from Table 403.3 and if so, what is that classification?

    FYI, 2021 IMC will add "and NFPA 99" to the end of 407.1. These facilities will have to comply with the IMC and ASHRAE 170 and NFPA 99 !!! Won't that be fun :)
     
  2. Bryant

    Bryant Registered User

    Joined:
    Dec 19, 2018
    Messages:
    37
    Likes Received:
    1
    that is a lot to breath in at once :eek:
     
  3. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,225
    Likes Received:
    326
    IT seems that the IMC should have the requirements of ASHRAE 170 added to the tables if possible.
     
  4. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,815
    Likes Received:
    263
    % ~ % ~ %

    Possibly, something akin to a small Conference Room.

    % ~ % ~ %
     