• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Mezzanine Clearance

FyrBldgGuy

Silver Member
Joined
Oct 19, 2009
Messages
356
The code requires 7 foot above and below a mezzanine. Do you consider the structural steel, such as knee braces, gussets, etc. when determining the 7 feet?
 
Based upon the provisions of Section 1208.2 and 505.1, 7 foot clear is required. Structure should not impinge in the required 7 foot head clearance.
 
I would allow it with some kind of permanent barrier installed at the area of the encroachments.

Then I would deduct the barriers from the fire area and the aggregate areas.
 
Those are not "ceiling" elements. They are projections from the ceiling so the beams and gussets, knee bracing and such do not affect the ceiling height. However, if the mezzanine is occupied then the projections cannot be closer to the floor than 6'-8" at their lowest.
 