REGISTERED
Michigan building Code 2021,
I have a small after school care building that they are wanting to have a mezzanine in the space. The space is open to below and used for tv and lounge type activities. Total building square footage is only 7000 sf with the mezzanine only being 1500 sf.
I am not seeing how I can consider this anything other than and Educational use group as a Daycare since its minors being supervised. Section 903.2.3 Group E states
An automatic sprinkler system shall be provided for Group E occupancies as follows:
Now with it being a mezzanine, its considered a portion of the floor below and shall not contribute to the building area or number of stories. And there is egress at the bottom of the stairs that are open to the floor. So with this, do I need to fire suppress the mezzanine space?
I have a small after school care building that they are wanting to have a mezzanine in the space. The space is open to below and used for tv and lounge type activities. Total building square footage is only 7000 sf with the mezzanine only being 1500 sf.
I am not seeing how I can consider this anything other than and Educational use group as a Daycare since its minors being supervised. Section 903.2.3 Group E states
An automatic sprinkler system shall be provided for Group E occupancies as follows:
- Throughout all Group E fire areas greater than 12,000 square feet (1115 m2) in area.
- The Group E fire area is located on a floor other than a level of exit discharge serving such occupancies.
Exception: In buildings where every classroom has not fewer than one exterior exit door at ground level, an automatic sprinkler system is not required in any area below the lowest level of exit discharge serving that area. - The Group E fire area has an occupant load of 300 or more.
Now with it being a mezzanine, its considered a portion of the floor below and shall not contribute to the building area or number of stories. And there is egress at the bottom of the stairs that are open to the floor. So with this, do I need to fire suppress the mezzanine space?