• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Mini / self storage doors, storage Doors

sergoodo

Registered User
Joined
Oct 27, 2009
Messages
298
12’x 60’ storage (3 occupants) with only (1) rollup 8’x8’ door exit from space. Exception #1 applicable and Exception #6 not applicable? No requirement to apply #6 or take additional exception?

2015 IBC

1010.1.2 Door swing.

Egress doors shall be of the pivoted or side-hinged swinging type.
Exceptions:
1. Private garages, office areas, factory and storage areas with an occupant load of 10 or less.
6. In other than Group H occupancies, special purpose horizontal sliding, accordion or folding door assemblies complying with Section 1010.1.4.3.
 
Exception 1 applies. Exception 6 only applies to horizontally moving doors regardless of occupant load. Exception 6 is what door manufacturers like Won-Door uses for compliance.
 
Thanks. After taking exception #1 where does code tie into/link the requirements: simple operation opening, force required to open, fire ratings? Currently see a disconnect.
 
Thanks. After taking exception #1 where does code tie into/link the requirements: simple operation opening, force required to open, fire ratings? Currently see a disconnect.


Not required?

Are you talking interior units??

Multi story building??

Sprinklers ??
 
Not required?
Are you talking interior units??
Multi story building??
Sprinklers ??
standalone struct
single story
non sprinklered

additional info for: "Not required?"
Project has 2 Design problem solutions:
1)Buy 8x40 refrigerated shipping container to store perishables.
2) Construct slighty larger 14x60 (more functional) refridgerated portable storage building.

If we take #1 exception, I cannot find where IBC requires: operability, opening force etc. for the 14x60 storage. 14x60 required to comply with IBC, ADA is not a factor, this is temporary additional employee work area.
 