KHL
SAWHORSE
2018 IBC, Mixed Use (A2 & R2), non-separated, type VB, fully sprinkled NFPA 13
1020.4 = 20 ft dead ends max.
Then Exception 2 allows R2 to have 50 ft dead ends if sprinkled.
A2 is not included in any exception.
So question is, in this mixed use non-separated scenario, would it still be acceptable to use the R2 exception in the R2 areas of the building? Or can you not take the exception because the A2 is a max of 20 ft?
1020.4 = 20 ft dead ends max.
Then Exception 2 allows R2 to have 50 ft dead ends if sprinkled.
A2 is not included in any exception.
So question is, in this mixed use non-separated scenario, would it still be acceptable to use the R2 exception in the R2 areas of the building? Or can you not take the exception because the A2 is a max of 20 ft?