Hi,
Let me thank everyone in advance here, this forum is loaded with good advice so far.
To start with my building is Type II-B Non sprinkled. It is a metal warehouse with wood framed offices (about 15-20%).
My offices are used to do wholesale sales calls and engineering of wheels.
My storage is a majority alloy wheels stored in cardboard boxes. We do have a couple metal racks, but not many, and the usual crap such as brooms, some of my christmas decor...
So we are Mixed use. B of course for the interior offices. Then the warehouse with wheels in cardboard boxes, should this be S-1 or S-2 ? I see Metal and steel objects and autoshops in S-2, but see cardboard boxes in S-1.
Here is the kicker, which unless I am reading it incorrect S-1 requires no fire barrier or wall, where as S-2 does. How is S-1 (moderate) require no fire barrier, where as S-2 (low) requires two hour? I get this by referring to table 508.4
I read about this on another thread on a older code here, but still it seems screwy:
www.eng-tips.com
Let me thank everyone in advance here, this forum is loaded with good advice so far.
To start with my building is Type II-B Non sprinkled. It is a metal warehouse with wood framed offices (about 15-20%).
My offices are used to do wholesale sales calls and engineering of wheels.
My storage is a majority alloy wheels stored in cardboard boxes. We do have a couple metal racks, but not many, and the usual crap such as brooms, some of my christmas decor...
So we are Mixed use. B of course for the interior offices. Then the warehouse with wheels in cardboard boxes, should this be S-1 or S-2 ? I see Metal and steel objects and autoshops in S-2, but see cardboard boxes in S-1.
Here is the kicker, which unless I am reading it incorrect S-1 requires no fire barrier or wall, where as S-2 does. How is S-1 (moderate) require no fire barrier, where as S-2 (low) requires two hour? I get this by referring to table 508.4
I read about this on another thread on a older code here, but still it seems screwy:
Storage occupancy: separation from other occupancies, and S-1 vs S-2 - NFPA (fire) Code Issues - Eng-Tips
There is something I don't understand with the IBC 2006, Table 508.3.3. This is kind of related to NFPA codes, so not out of line to post here.. An example: A s