We have a mobile home park built on the side of a hill, actually base of a mountain that has clusters of services from the POCO with about 8-12 meter bases mounted on posts framed out, depending on the area they serve. Because they are located behind the lots and there are different length mobile homes, some of the runs from the meter base disconnects are 60-80' away and certainly not within site. FEMA has renovated this area for post flood victims and now have to install disconnects between the units to feed the sub panels in the mobile homes. They too have a rule for a disconnect to be within site and so many feet of the mobile home.
So, this is what we have.
The service group of meters and disconnects is already installed and has a GE system.
The new posts with plywood that supports (structure) the disconnects between the units also have a grounding electrode system. They are fed by PVC pipe. Then the feeder goes from that disconnect to the mobile home which is another structure and they have their own grounding electrode system.
We have had some debate back and forth but the inspector that works for me that is in charge of the project and working with FEMA says that FEMA believes the ground rods are required because there are 3 separate structures and he concurs. We initially had some resistance to this by the contractor who has since backed off due to FEMA saying this is what they want and my guy confirming it.
I have had some discussion with other inspectors that are trying to say that the mobile home is not a structure, therefore does not need rods and the pole and frame that holds the mid point disconnect is not a structure so the only rods should be at the service disconnect,
What say thee?
So, this is what we have.
The service group of meters and disconnects is already installed and has a GE system.
The new posts with plywood that supports (structure) the disconnects between the units also have a grounding electrode system. They are fed by PVC pipe. Then the feeder goes from that disconnect to the mobile home which is another structure and they have their own grounding electrode system.
We have had some debate back and forth but the inspector that works for me that is in charge of the project and working with FEMA says that FEMA believes the ground rods are required because there are 3 separate structures and he concurs. We initially had some resistance to this by the contractor who has since backed off due to FEMA saying this is what they want and my guy confirming it.
I have had some discussion with other inspectors that are trying to say that the mobile home is not a structure, therefore does not need rods and the pole and frame that holds the mid point disconnect is not a structure so the only rods should be at the service disconnect,
What say thee?