Multi-Wire Branch Circuits Code Requirements Explained - NEC 2023
Guide to Multiwire Branch Circuits in the 2023 NFPA 70 NEC 210.4210.4 Multiwire Branch Circuits A. General
Multiwire branch circuits are permitted and can be considered as multiple circuits.
All conductors must originate from the equipment with the branch-circuit overcurrent protective device, except as specified in 300.3(B)(4).
Informational Notes:
3-phase, 4-wire, wye-connected systems may experience high harmonic currents on the neutral conductor due to nonlinear loads.
Continuity of grounded conductors on multiwire circuits is addressed in 300.13(B).
Enhanced Content:
Multiwire branch circuits can serve dual purposes, such as providing two appliance circuits in kitchen countertops.
Issues with harmonic currents may arise from devices like computers and printers which may exceed the load current itself.
Refer to 310.15(E) for guidelines on neutral conductor ampacity.
B. Disconnecting Means
A means to simultaneously disconnect all ungrounded conductors must be provided at the circuit origin.
Informational Note: Single-pole circuit breakers as disconnecting means are discussed in 240.15(B).
Options for disconnecting include:
For single-phase: two single-pole breakers with a handle tie or a 2-pole breaker.
For 3-phase: a 3-pole breaker, three single-pole breakers with a handle tie, or a 3-pole switch with protection.
C. Line-to-Neutral Loads
Multiwire branch circuits should only supply line-to-neutral loads.
Exceptions:
Circuits supplying only one equipment can supply line-to-line loads.
Permitted line-to-line loads if a device opens all ungrounded conductors simultaneously.
Enhanced Content:
Common configurations include 120/240-volt, single-phase systems often found in residential applications.
Benefits include reduced wire use, easier balancing, and less voltage drop.
Care must be taken with high-leg delta systems, especially with phase B (marked orange).
D. Grouping
Ungrounded and grounded conductors of each circuit must be grouped as specified in 200.4(B).
See Also:
210.19, 210.4(A), 240.15(B)(1), 300.13(B) for further reading on voltage drop, 3-phase system neutrals, and circuit protection specifics.