Guide to Multiwire Branch Circuits in the 2023 NFPA 70 NEC 210.4​

210.4 Multiwire Branch Circuits

A. General
  • Multiwire branch circuits are permitted and can be considered as multiple circuits.
  • All conductors must originate from the equipment with the branch-circuit overcurrent protective device, except as specified in 300.3(B)(4).
  • Informational Notes:
    1. 3-phase, 4-wire, wye-connected systems may experience high harmonic currents on the neutral conductor due to nonlinear loads.
    2. Continuity of grounded conductors on multiwire circuits is addressed in 300.13(B).
Enhanced Content:
  • Multiwire branch circuits can serve dual purposes, such as providing two appliance circuits in kitchen countertops.
  • Issues with harmonic currents may arise from devices like computers and printers which may exceed the load current itself.
  • Refer to 310.15(E) for guidelines on neutral conductor ampacity.
B. Disconnecting Means
  • A means to simultaneously disconnect all ungrounded conductors must be provided at the circuit origin.
  • Informational Note: Single-pole circuit breakers as disconnecting means are discussed in 240.15(B).
  • Options for disconnecting include:
    • For single-phase: two single-pole breakers with a handle tie or a 2-pole breaker.
    • For 3-phase: a 3-pole breaker, three single-pole breakers with a handle tie, or a 3-pole switch with protection.
C. Line-to-Neutral Loads
  • Multiwire branch circuits should only supply line-to-neutral loads.
  • Exceptions:
    1. Circuits supplying only one equipment can supply line-to-line loads.
    2. Permitted line-to-line loads if a device opens all ungrounded conductors simultaneously.
  • Enhanced Content:
    • Common configurations include 120/240-volt, single-phase systems often found in residential applications.
    • Benefits include reduced wire use, easier balancing, and less voltage drop.
    • Care must be taken with high-leg delta systems, especially with phase B (marked orange).
D. Grouping
  • Ungrounded and grounded conductors of each circuit must be grouped as specified in 200.4(B).
See Also:
  • 210.19, 210.4(A), 240.15(B)(1), 300.13(B) for further reading on voltage drop, 3-phase system neutrals, and circuit protection specifics.
 