• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Multifamily air leakage testing

Sifu

SAWHORSE
Joined
Sep 3, 2011
Messages
2,773
I have a 4 story above grade plane R2. The way I read the energy code they are not required to conduct leakage testing since they are considered a commercial building in the eyes of the IECC, and they can choose to follow the prescriptive requirements of IECC 402.5.1 through 402.5.8. But, if they were 3 stories above grade plane they would be required to have testing. Am I reading this correctly?
 
You are correct
2018 IECC
COMMERCIAL BUILDING. For this code, all buildings that are not included in the definition of “Residential building.”
 