This is indoors ....right?
The violation is what you can see, not what you can'tFitting yes.
Any splicing of wires?
Not an electrical inspector (WA State L&I is AHJ), but looks to me that the clamp has been tightened all the way down and has not clamped onto the LFNC.
The clamp, if I had to speculate, is not for use with LFNC.
As I don't typically look at electrical, I'd like to get your experienced insight... isn't the coupling in the original picture for EMT to FMC? LFNC couplings are typically a compression bushing I believe.I noticed the maxed out clamp too....now that would be worth a correction. If the conduit had been wrapped with tape until it was large enough to work with the clamp I doubt that I would write a correction....
You are correct. The location would not require liquid tight conduit and the fitting worked except for being loose.....As I don't typically look at electrical, I'd like to get your experienced insight... isn't the coupling in the original picture for EMT to FMC? LFNC couplings are typically a compression bushing I believe.
I believe that the coupling in the OP is for FMC. For LFNC, this would be the appropriate coupling to use.
![]()
https://www.graybar.com/store/en/gb/zinc-plated-steel-flex-to-emt-combination-coupling