Michael.L
This is for commercial tenant improvements for a food service establishment. My city is currently operating under the 2015 International Fuel Gas Code.
Section 406.4.1 of the 2015 IFC reads as follows:
Our gas service is supplied by the utility company at less than 10-in w.c. (IIRC, the utility rep told me they could only give us ~7.5-in w.c.). Our gas appliances are rated for a maximum of 14-in w.c.
Even assuming that the gas were supplied at the maximum acceptable (14-in w.c.), that's only ~0.5 psi and 1½ times that is 0.75 psi. So according to 406.4.1, the correct test pressure should be "not less than 3 psig." Agreed?
There is an Ansul gas valve in the piping that states on the label, "Max pressure 10 psi." So I precharged the gas piping to 10 psi for the inspection. The inspector refused to pass our gas piping, stating that "All low-pressure gas line tests must be performed at 20 psi." When I pointed out the limitation on the Ansul valve, he told me to remove it from the piping and bypass it for the test, then reinstall it after and bubble test it for leaks.
I contacted Ansul tech support and the engineer confirmed that we should not test above 10 psi with their valve in the line. He also agreed that testing at 10 psi would be far greater than necessary since that's over 20 times the service pressure.
I'd rather not get into a pissing match with the inspector, especially since I already (mildly) objected to the 20 psi test and he emphatically stated that it was required. (I knew the IFC did not require a 20 psi test, but I was not expecting this from him so I didn't have the code reference ready to challenge him). On the other hand, I do not wish to have our (perfectly assembled and pressure-tested) piping disassembled to meet his arbitrary 20 psi test requirement.
I'm curious what other inspectors require for gas piping pressure tests. I'd also like recommendations on how to proceed. Thanks.
406.4.1 Test Pressure
The test pressure to be used shall not be less than 1½ times the proposed maximum working pressure, but not less than 3 psig (20 kPa gauge), irrespective of design pressure. Where the test pressure exceeds 125 psig (862 kPa gauge), the test pressure shall not exceed a value that produces a hoop stress in the piping greater than 50 percent of the specified minimum yield strength of the pipe.