Mech
REGISTERED
2009 IMC (& IBC)
Warehouse building is supplied with outside air via natural gas direct fired make-up air units. The amount of OA provided exceeds the code requirement by about 2400 cfm.
The internal 340 sq ft shipping office has one door, which opens into the warehouse, and the designer's plan is to utilize "natural ventilation" (airflow through the man door) from the mechanically ventilated warehouse, not the outside. The door opening exceeds 4% of the office floor area (area to be ventilated.)
Would you allow this?
Would you allow this under Section 105.2 Alternative materials, methods, equipment, and appliances?
402.1 Natural ventilation. Natural ventilation of an occupied space shall be through windows, doors, louvers or other openings to the outdoors. The operating mechanism for such openings shall be provided with ready access so that the openings are readily controllable by the building occupants.
402.2 Ventilation area required. The minimum openable area to the outdoors shall be 4 percent of the floor area being ventilated.
105.2 Alternative materials, methods, equipment and appliances. The provisions of this code are not intended to prevent the installation of any material or to prohibit any method of construction not specifically prescribed by this code, provided that any such alternative has been approved. An alternative material or method of construction shall be approved where the code official finds that the proposed design is satisfactory and complies with the intent of the provisions of this code, and that the material, method or work offered is, for the purpose intended, at least the equivalent of that prescribed in this code in quality, strength, effectiveness, fire resistance, durability and safety.
Thanks in advance.
Warehouse building is supplied with outside air via natural gas direct fired make-up air units. The amount of OA provided exceeds the code requirement by about 2400 cfm.
The internal 340 sq ft shipping office has one door, which opens into the warehouse, and the designer's plan is to utilize "natural ventilation" (airflow through the man door) from the mechanically ventilated warehouse, not the outside. The door opening exceeds 4% of the office floor area (area to be ventilated.)
Would you allow this?
Would you allow this under Section 105.2 Alternative materials, methods, equipment, and appliances?
402.1 Natural ventilation. Natural ventilation of an occupied space shall be through windows, doors, louvers or other openings to the outdoors. The operating mechanism for such openings shall be provided with ready access so that the openings are readily controllable by the building occupants.
402.2 Ventilation area required. The minimum openable area to the outdoors shall be 4 percent of the floor area being ventilated.
105.2 Alternative materials, methods, equipment and appliances. The provisions of this code are not intended to prevent the installation of any material or to prohibit any method of construction not specifically prescribed by this code, provided that any such alternative has been approved. An alternative material or method of construction shall be approved where the code official finds that the proposed design is satisfactory and complies with the intent of the provisions of this code, and that the material, method or work offered is, for the purpose intended, at least the equivalent of that prescribed in this code in quality, strength, effectiveness, fire resistance, durability and safety.
Thanks in advance.