I was about to take the Repair Garage Ventilation thread off track, so I thought I would reel it back in and start a new one.
Code references: IMC 401.3 "Ventilation shall be provided during the periods that the room or space is occupied.". IBC 1204.1 "Interior spaces intended for human occupancy shall be provided with active or passive space-heating systems capable of maintaining a minimum indoor temperature of 68°F (20°C) at a point 3 feet (914 mm) above the floor on the design heating day.
Exception: Interior spaces where the primary purpose is not associated with human comfort."
It is my opinion that the simple version of opening windows for natural ventilation as the exclusive means of code required ventilation is not allowed unless the DP can show how the IBC required temperature in the space is maintained while the windows are open whenever occupied as required by the IMC.
There are options available to the DP such as natural ventilation airshafts with some means of tempering the air, or operable windows with end switches that enable mechanical ventilation when closed and disable it when open, but just plain operable windows is not code compliant.
Note IMC 401.3 does not say "The capability to control ventilation shall be provided..." or "The occupants shall have the opportunity to control ventilation...".
Code references: IMC 401.3 "Ventilation shall be provided during the periods that the room or space is occupied.". IBC 1204.1 "Interior spaces intended for human occupancy shall be provided with active or passive space-heating systems capable of maintaining a minimum indoor temperature of 68°F (20°C) at a point 3 feet (914 mm) above the floor on the design heating day.
Exception: Interior spaces where the primary purpose is not associated with human comfort."
It is my opinion that the simple version of opening windows for natural ventilation as the exclusive means of code required ventilation is not allowed unless the DP can show how the IBC required temperature in the space is maintained while the windows are open whenever occupied as required by the IMC.
There are options available to the DP such as natural ventilation airshafts with some means of tempering the air, or operable windows with end switches that enable mechanical ventilation when closed and disable it when open, but just plain operable windows is not code compliant.
Note IMC 401.3 does not say "The capability to control ventilation shall be provided..." or "The occupants shall have the opportunity to control ventilation...".